New siga-ps detector installed and show this message from SDU :
"Max. quiescent value threshold Optical sensor exceed - dirtied"
the siga-ps are new and totally clean. Anybody see this ?
NEW SIGA-PS ON THE LOOP - DIRTIED MESSAGE
Re: NEW SIGA-PS ON THE LOOP - DIRTIED MESSAGE
i had the same problem, i replaced the detector, after an hour the trouble return on the same location, the problem maybe is not on the detector it may be on the wiring
Re: NEW SIGA-PS ON THE LOOP - DIRTIED MESSAGE
just wait 24 hours, because the new detector receive the programming of the panel with data from the old detector