I think the ducts are on the same SLC. Thanks for the good advise. We will try another loop. I'm still skeptical of the FA MC cable.

Thanks so much
deestech
Posts: 7
Joined: Tue Jul 28, 2015 12:42 pm

Re: Proper FA wire for EST- 3 devices

Post by deestech »

I have a concern regarding DGP panels. We did not add any DGP to our new FA system, and the FA cable is a bit long. Will adding DGP solve the issue.

Are the new duct detectors (47 units) going into alarm (at random) because there is no DGP installed?

Thank you
old_tech
Posts: 78
Joined: Wed Jan 23, 2013 7:30 am

Re: Proper FA wire for EST- 3 devices

Post by old_tech »

siga-sd's are the problem. Keep swapping the bad ones out, after 6 months or so you wont have any more problems. same with mapping fault and siga2-ps detectors.
pyrosucks
Posts: 106
Joined: Wed Feb 23, 2011 9:08 am

Re: Proper FA wire for EST- 3 devices

Post by pyrosucks »

Try replacing the slc card. Had a new system we just did and it ended up being the cause. I was getting random comm faults on detectors.
pyrosucks
Posts: 106
Joined: Wed Feb 23, 2011 9:08 am

Re: Proper FA wire for EST- 3 devices

Post by pyrosucks »

I would not see the wire as an issue unless you are talking 10k feet plus
Leo
Site Admin
Posts: 889
Joined: Thu Dec 11, 2008 7:52 am

Re: Proper FA wire for EST- 3 devices

Post by Leo »

*** found this, it may help
*** check attached doc





****** copy pasted doc *******
Tech Notes - Fix Bulletin - Technical Training News - Purchasing News - CDC Update - Quality Alert
August 22, 2008 1-800-390-6236/E-mail:techsupportnj@adt.com Vol. 11 – No. 2
GE SuperDuct Smoke Detectors
ADT has received notification from GE Security that their SuperDuct Smoke Detectors are generating
false alarms and trouble signals when excessive condensation from unconditioned outside air enters
the unit. SuperDuct Smoke Detectors that are not installed in unconditioned outside air entrances are
not affected. GE Security engineering is working on a solution to this issue and will publish a quality
alert when it is available.
Affected SuperDuct Models
- SIGA-SD Intelligent SuperDuct Smoke Detector, equipped with a Signature Series
photoelectric sensor.
- SD-2W Conventional SuperDuct Smoke Detector, 2-Wire.
What to Do
1. SuperDuct Smoke Detectors that experienced false alarms and trouble signals caused by
excessive condensation will need to be replaced with a different smoke detector model as
indicated in the table below.
Affected Model Replacement Model
SIGA-SD SIGA-DH Intelligent Duct Smoke Detector Housing
SD-2W 6260A-CU Housing and EC30DU-3 Detector
2. Return affected SuperDuct Smoke Detectors to manufacturer for credit using the standard RMA
procedure. Use the link below to access the RMA form:
http://insideadt.com/main/it/bizservice ... endors.pdf
3. For all new installations, do not install SIGA-SD or SD-2W SuperDuct Smoke Detectors at
unconditioned outside air entrances that have excessive condensation. Use replacement
model smoke detectors.
For any questions concerning this document call GE Technical Support at (800) 655-4497 or e-mail at
est.techsupport@ge.com
RECIPIENTS: Distribute this QUALITY ALERT to individuals who will benefit from this
information and post it on the Branch’s Bulletin Board.
Visit the Product Support web page on InsideADT.com (in the “DEPARTMENTS” group) for
access to all of the Product Support information.
Attachments
superducts-est.pdf
(62.43 KiB) Downloaded 374 times