Vista-32FB program as Fire Panel
Posted: Sun Feb 19, 2012 2:31 pm
Vista-32FB Programming for a fire system
default master code - 5140
Ademco 5140DLM Backup Dialer - two main program changes
3*30 = 1,1 Main,Backup, 3*30 = 0,0 both dialers are disabled
Zone 974 dialer 1 zone type = 19
Zone 975 dialer 2 zone type = 19 ( 24 hour monitor of the phone line)
*32 Account number = ie. 9999 09 09 09 09
*33 first Receiver phone number = ie. 18774441234 end with *
*34 Second Receiver phone number
1*26 will make the "A" speedkey fire alarm silence. = 33,00,00,00 = A,B,C,D (HIT THE A BUTTON TO SILENCE BELLS)
*45 dialer format, default is 1, contact ID =1
3*13 = 1, If Value tamper is normal closed and goes open when active
3*61 = 2, 4 wire smokes to use aux relay to reset power.
3*00 = 1, 0=CHECK; 1=TRBL (the word CHECK is a admeco thing and I don't like it.)
*27 = 024, 24 hour timer test
*83 = 00 12 00, next timer test in 12 hours
change Time and Date - code # 63
default master code - 5140
Ademco 5140DLM Backup Dialer - two main program changes
3*30 = 1,1 Main,Backup, 3*30 = 0,0 both dialers are disabled
Zone 974 dialer 1 zone type = 19
Zone 975 dialer 2 zone type = 19 ( 24 hour monitor of the phone line)
*32 Account number = ie. 9999 09 09 09 09
*33 first Receiver phone number = ie. 18774441234 end with *
*34 Second Receiver phone number
1*26 will make the "A" speedkey fire alarm silence. = 33,00,00,00 = A,B,C,D (HIT THE A BUTTON TO SILENCE BELLS)
*45 dialer format, default is 1, contact ID =1
3*13 = 1, If Value tamper is normal closed and goes open when active
3*61 = 2, 4 wire smokes to use aux relay to reset power.
3*00 = 1, 0=CHECK; 1=TRBL (the word CHECK is a admeco thing and I don't like it.)
*27 = 024, 24 hour timer test
*83 = 00 12 00, next timer test in 12 hours
change Time and Date - code # 63