Vista-32FB Programming for a fire system
default master code - 5140
Ademco 5140DLM Backup Dialer - two main program changes
3*30 = 1,1 Main,Backup, 3*30 = 0,0 both dialers are disabled
Zone 974 dialer 1 zone type = 19
Zone 975 dialer 2 zone type = 19 ( 24 hour monitor of the phone line)
*32 Account number = ie. 9999 09 09 09 09
*33 first Receiver phone number = ie. 18774441234 end with *
*34 Second Receiver phone number
1*26 will make the "A" speedkey fire alarm silence. = 33,00,00,00 = A,B,C,D (HIT THE A BUTTON TO SILENCE BELLS)
*45 dialer format, default is 1, contact ID =1
3*13 = 1, If Value tamper is normal closed and goes open when active
3*61 = 2, 4 wire smokes to use aux relay to reset power.
3*00 = 1, 0=CHECK; 1=TRBL (the word CHECK is a admeco thing and I don't like it.)
*27 = 024, 24 hour timer test
*83 = 00 12 00, next timer test in 12 hours
change Time and Date - code # 63
Vista-32FB program as Fire Panel
Jump to
- General Comments/How To Register
- ----- F i r e -----
- ↳ MANUALS
- ↳ NICET, NPFA72/70, State License
- ↳ NPFA72/70
- ↳ UTC - EST
- ↳ License,Dongle & Software Certificate
- ↳ EST3
- ↳ EST4
- ↳ EST3 Rules
- ↳ I/O panels
- ↳ QuickStart
- ↳ FireWorks
- ↳ EST2
- ↳ Misc/Devices
- ↳ IRC3
- ↳ Notifier
- ↳ Fire Panels - 640,2020,3030
- ↳ ONYXWorks
- ↳ FireLite
- ↳ SilentKnight
- ↳ Ademco - V32FB
- ↳ Fire Alarm Inspection
- ↳ Other FACP
- ↳ Duct Detectors
- ---- C a r d A c c e s s ----
- ↳ GE - Secure Perfect, Micro5
- ↳ Facility Commander/Secure Perfect
- ↳ Hardware
- ↳ Honeywell - Winpak
- ↳ honeywellaccess.com
- ↳ HoneyWell - ProWatch
- ↳ HoneyWellIntegrated.com
- ↳ Kantech
- ↳ Readers
- ↳ hidglobal.com
- ↳ HoneyWellintegrated.com - readers
- ↳ honeywellaccess.com - readers
- ↳ Card Access Systems
- ↳ Credentials
- ---- Other Systems ----
- ↳ Other Systems, DVR, Camera,
- ↳ communications protocol - RS232 RS485 RS422 TCP/IP Networking
- Heliostat
- ↳ Heliostat
- ↳ heliostat.us