NEW SIGA-PS ON THE LOOP - DIRTIED MESSAGE

Posted: Tue Dec 20, 2011 11:11 am
by gmcorreia
New siga-ps detector installed and show this message from SDU :

"Max. quiescent value threshold Optical sensor exceed - dirtied"

the siga-ps are new and totally clean. Anybody see this ?

Re: NEW SIGA-PS ON THE LOOP - DIRTIED MESSAGE

Posted: Tue Dec 20, 2011 8:08 pm
by anthony08
i had the same problem, i replaced the detector, after an hour the trouble return on the same location, the problem maybe is not on the detector it may be on the wiring

Re: NEW SIGA-PS ON THE LOOP - DIRTIED MESSAGE

Posted: Wed Dec 21, 2011 7:02 pm
by Sam
just wait 24 hours, because the new detector receive the programming of the panel with data from the old detector