NFPA90A - Duct Detector's - supply greater than 2,000
Posted: Mon Aug 17, 2009 9:13 pm
Duct Detector - 101
Supervisory or Alarm? myself and everyone I have spoken to makes them alarms
NFPA72 Tells you how to mount it.
90A defines a need for duct detectors downstream of all filters, supply fans with capacities greater than 2,000 cfm.
The same goes for those of return fans with a capacity greater than 15,000 cfm.
Also Duct-mounted smoke detectors are required in each return duct inlet that serves more than one story for systems with a capacity of greater than 15,000 cfm.
Q&A GOOD STUFF - http://findarticles.com/p/articles/mi_q ... _n8851155/
INFORMATION SHEET - http://www.lasvegasnevada.gov/files/duc ... elines.pdf
Duct Application - http://www.systemsensor.com/pdf/A05-1004.pdf
The Efficacy of Duct Smoke Detection - http://www.fpemag.com/archives/article. ... d=35&i=195
Supervisory or Alarm? myself and everyone I have spoken to makes them alarms
NFPA72 Tells you how to mount it.
90A defines a need for duct detectors downstream of all filters, supply fans with capacities greater than 2,000 cfm.
The same goes for those of return fans with a capacity greater than 15,000 cfm.
Also Duct-mounted smoke detectors are required in each return duct inlet that serves more than one story for systems with a capacity of greater than 15,000 cfm.