Setting the FDU-80 LCD-80F for multiple units is tricky
If you are installing multiple units wire the Annunciator at panel, get them working right, then remote the units
WIRING: this Annunciator requires 2 wires for power and 4 wires for data/comm (TOTAL OF 6 WIRES FOR ONE)
FDU-80 LCD-80F Wiring terminals
1-(out+)white
2-(in+)red
3-(out-)green
4-(out+)black
**** Wiring Multiple units ****
wired from IN -> OUT -> IN -> OUT one big loop.
dip Switch: POWER CYCLE AFTER CHANGES for switch 3!
1 - off key is needed, on no key
2 - piezo, on sounder on, off sounder off
3 - ON if only 1 FDU-80,
3 - if multiple Annunciator are used then only the last is ON (very important) the FDU-80 that feeds the FACP IN terminals
4-6 OFF
note:
1. SW The FDU-80 LCD-80F mimics the main FACP display
2. There is no Addressing of the FDU-80 LCD-80F
*************** MS-9600 MS-9200UD PROGRAMMING ********
*************** 3030 PROGRAMMING ***NFS2-3030 NFS-32030*****
TB9: RDP RS485 on the 3030 panel is a 4 wire connection
FDU-80 Verifire tool settings: LCD-80 Terminal Mode (checked)
**** Wiring for ONE FDU-80 ****
3030 TB9:RDP Terminals (left to right)
in+ white
in- green
out+ red
out- black
Terminal Options.
LCD-80 Terminal Mode. (NCA-2/NCA) Enable if the LCD-80 will be used in terminal mode. LCD-160 programming is not allowed; the Remote Display menu tab disappears if this choice is selected. Refer to the NCA-2/NCA and LCD-80 Installation Manuals for more information.
LCD80F LCD-80 LCD80 LCD-80F FDU-80 FDU80
FDU-80 LCD-80F INSTALLATION
FDU-80 LCD-80F INSTALLATION
- Attachments
-
- DN_6820 LCD-80F - FDU-80 DATASHEET.pdf
- (229.1 KiB) Downloaded 613 times
-
- FDU80 LDC-80F MMANUAL.pdf
- (745.98 KiB) Downloaded 662 times