Rule for EST3

Post Reply
briac
Posts: 93
Joined: Sat Jul 28, 2012 10:16 am
Location: GMT+3

Re: Rule for EST3

Post by briac »

hi,
The first one(smoke and pull) you activate it on simple rules like:
ALM_SMK*: ON AUDIBLE*
ALM_PULL*:ON AUDIBLE*
The second one you use "and group" with active device number 2 to activate the releasing module.
R1:{FOR RESET}
RESET REL PREALARM
R2:RE
RESET SOLENOID
AND_SMK:
PRE_AUDIBLE{to activate the prealarm of the siga REL}
SOL_RELEASE{to activate the releasing }

I think that's the main line of you program.

refer to this post for SIGA REL programing
http://www.thealarmtech.com/forum/viewt ... =33&t=1196
hope to help you.
khorasani
Posts: 37
Joined: Fri Sep 19, 2014 9:25 am

Re: Rule for EST3

Post by khorasani »

Many Thanks my friend:)
khorasani
Posts: 37
Joined: Fri Sep 19, 2014 9:25 am

Re: Rule for EST3

Post by khorasani »

briac wrote:hi,
The first one(smoke and pull) you activate it on simple rules like:
ALM_SMK*: ON AUDIBLE*
ALM_PULL*:ON AUDIBLE*
The second one you use "and group" with active device number 2 to activate the releasing module.
R1:{FOR RESET}
RESET REL PREALARM
R2:RE
RESET SOLENOID
AND_SMK:
PRE_AUDIBLE{to activate the prealarm of the siga REL}
SOL_RELEASE{to activate the releasing }

I think that's the main line of you program.

refer to this post for SIGA REL programing
http://www.thealarmtech.com/forum/viewt ... =33&t=1196
hope to help you.



many thanks my friend:)
behzad
Posts: 13
Joined: Mon Jan 09, 2023 6:11 am

Re: Rule for EST3

Post by behzad »

HI,COULD YOU SEND ME EMAIL IF YOU IRANIAN GUYS,
Behzad_babazade@yahoo.com
shabirhaneefa
Posts: 13
Joined: Fri Oct 28, 2022 5:06 am

Re: Rule for EST3

Post by shabirhaneefa »

Anybody can help me to set rule for sounder activation after 30 sec
ericflorendo
Posts: 13
Joined: Mon Feb 04, 2013 8:04 pm

Re: Rule for EST3

Post by ericflorendo »

Alarm '*_*':
DLYA 30,
ON 'LEV*_*_SOUNDER*';
khorasani
Posts: 37
Joined: Fri Sep 19, 2014 9:25 am

Rule for EST3

Post by khorasani »

Hi everybody,
I want to write rule for 3 smoke detectors,1 manual call point , 1 sounder and 1 release module ;if any of smoke detectors or manual call point activated then the sounder activate and if two smoke detectors activated simoltaneously then activate the sounder and release module .
any one can help me please?
many thanks for useful helps.
Anas
Posts: 1
Joined: Thu Nov 28, 2024 10:31 pm

Rule for EST3

Post by Anas »

Hi
I have a site . There are some emergency doors are connected to the fire panel. When the fire panel activates the automatic locks opens and the in built sounders of Automatic doors will trigger. But when I make silence the panel will silenced and the doors still sounds. So I found solution. We have already installed a CR for operating the door controls that will only reset when panel get reset. If we add an additional cr to the sounder line when I press the silence button it will stop the sounder only and door need to remain open until the panel reset.,.... Please help me to create a rule that will not operate in the fire and only operate the cr module while pressing silence button..... Thanks
Post Reply