hi,
The first one(smoke and pull) you activate it on simple rules like:
ALM_SMK*: ON AUDIBLE*
ALM_PULL*:ON AUDIBLE*
The second one you use "and group" with active device number 2 to activate the releasing module.
R1:{FOR RESET}
RESET REL PREALARM
R2:RE
RESET SOLENOID
AND_SMK:
PRE_AUDIBLE{to activate the prealarm of the siga REL}
SOL_RELEASE{to activate the releasing }
I think that's the main line of you program.
refer to this post for SIGA REL programing
http://www.thealarmtech.com/forum/viewt ... =33&t=1196
hope to help you.
Rule for EST3
Re: Rule for EST3
briac wrote:hi,
The first one(smoke and pull) you activate it on simple rules like:
ALM_SMK*: ON AUDIBLE*
ALM_PULL*:ON AUDIBLE*
The second one you use "and group" with active device number 2 to activate the releasing module.
R1:{FOR RESET}
RESET REL PREALARM
R2:RE
RESET SOLENOID
AND_SMK:
PRE_AUDIBLE{to activate the prealarm of the siga REL}
SOL_RELEASE{to activate the releasing }
I think that's the main line of you program.
refer to this post for SIGA REL programing
http://www.thealarmtech.com/forum/viewt ... =33&t=1196
hope to help you.
many thanks my friend:)
Re: Rule for EST3
HI,COULD YOU SEND ME EMAIL IF YOU IRANIAN GUYS,
Behzad_babazade@yahoo.com
Behzad_babazade@yahoo.com
-
- Posts: 13
- Joined: Fri Oct 28, 2022 5:06 am
Re: Rule for EST3
Anybody can help me to set rule for sounder activation after 30 sec
-
- Posts: 13
- Joined: Mon Feb 04, 2013 8:04 pm
Re: Rule for EST3
Alarm '*_*':
DLYA 30,
ON 'LEV*_*_SOUNDER*';
DLYA 30,
ON 'LEV*_*_SOUNDER*';
Rule for EST3
Hi everybody,
I want to write rule for 3 smoke detectors,1 manual call point , 1 sounder and 1 release module ;if any of smoke detectors or manual call point activated then the sounder activate and if two smoke detectors activated simoltaneously then activate the sounder and release module .
any one can help me please?
many thanks for useful helps.
I want to write rule for 3 smoke detectors,1 manual call point , 1 sounder and 1 release module ;if any of smoke detectors or manual call point activated then the sounder activate and if two smoke detectors activated simoltaneously then activate the sounder and release module .
any one can help me please?
many thanks for useful helps.
Rule for EST3
Hi
I have a site . There are some emergency doors are connected to the fire panel. When the fire panel activates the automatic locks opens and the in built sounders of Automatic doors will trigger. But when I make silence the panel will silenced and the doors still sounds. So I found solution. We have already installed a CR for operating the door controls that will only reset when panel get reset. If we add an additional cr to the sounder line when I press the silence button it will stop the sounder only and door need to remain open until the panel reset.,.... Please help me to create a rule that will not operate in the fire and only operate the cr module while pressing silence button..... Thanks
I have a site . There are some emergency doors are connected to the fire panel. When the fire panel activates the automatic locks opens and the in built sounders of Automatic doors will trigger. But when I make silence the panel will silenced and the doors still sounds. So I found solution. We have already installed a CR for operating the door controls that will only reset when panel get reset. If we add an additional cr to the sounder line when I press the silence button it will stop the sounder only and door need to remain open until the panel reset.,.... Please help me to create a rule that will not operate in the fire and only operate the cr module while pressing silence button..... Thanks