Search found 4 matches

by kelaa
Wed Nov 07, 2012 11:51 am
Forum: EST3
Topic: System capacity
Replies: 6
Views: 5699

Re: System capacity

neither the 3-REMICP nor 3-REMICA has the technical functionality that is desired. it is required that a selector switch be available at each point.
by kelaa
Mon Oct 29, 2012 8:18 am
Forum: EST3
Topic: System capacity
Replies: 6
Views: 5699

Re: System capacity

thanx Leo. I have 71 paging points. All points will require selective paging to various areas or departments. Had wished to limit the system to 1 network w/out having to interlink more than 1 system. Have already trimmed down the paging points to 71 and all are concidered essential. there is only 1 ...
by kelaa
Mon Oct 22, 2012 11:07 am
Forum: EST3
Topic: System capacity
Replies: 6
Views: 5699

Re: System capacity

Im hopiong so Leo. but Each paging point will be regarded as a node as its linked to the annunciator cpu. if i have more than 64 nodes (Max no. in Network) how do i make provisions for the extra nodes?
by kelaa
Fri Oct 19, 2012 9:10 am
Forum: EST3
Topic: System capacity
Replies: 6
Views: 5699

System capacity

Hey Guys! Im new to this system and want some clarification on the system capacity and application. Im working on a project where an ES 3 system shall be installed. Its a health care facility and intend to install more than 60 [/highlight][/highlight]paging points with annunciation at every nurse st...