- Fri Jul 06, 2012 4:10 pm
- Forum: EST3
- Topic: EST3 device sensitivity report printout
- Replies: 2
- Views: 4494
EST3 device sensitivity report printout
Can anyone tell me how to interpret the numbers being displayed DIRTY: in a sensitivity report for analog devices? Is it a percentage of being dirty or do you have to convert the number somehow to get the percentage of dirty for the device? Please see the print out attachment below
- Tue Feb 21, 2012 12:49 pm
- Forum: Other FACP
- Topic: new to the forum
- Replies: 6
- Views: 7795
Re: new to the forum
Welcome!
It sounds like you can be another valuable resource.
It sounds like you can be another valuable resource.
- Wed Jul 27, 2011 3:36 pm
- Forum: EST3
- Topic: Making audio files for ASU
- Replies: 1
- Views: 3452
Re: Making audio files for ASU
Try re-sampling the wav file @ 9600 in Goldwave. I have used this procedure for several messages used on our systems.
- Fri Apr 29, 2011 6:27 pm
- Forum: EST3
- Topic: Est3 CPU Groundfault
- Replies: 1
- Views: 3205
Re: Est3 CPU Groundfault
Yes, I a have had similar problem. We discovered that a printer cable on the port 2 of the 3rd panel in the network had an intermmittent ground. And it only showed up when we did a master reset. Check if RS232 ports. Also could be an intermittent ground on RS485 channel.
- Fri Apr 29, 2011 6:16 pm
- Forum: EST3
- Topic: SIGA-SD Maintenance Alert
- Replies: 8
- Views: 10834
Re: SIGA-SD Maintenance Alert
I have never restarted the card before I will give that a try. Thnx JimM
- Fri Apr 29, 2011 6:15 pm
- Forum: EST3
- Topic: SIGA-SD Maintenance Alert
- Replies: 8
- Views: 10834
Re: SIGA-SD Maintenance Alert
Sorry for the delay in replying. The answer is that I did not remove the SLC loop wiring when cleaning. The device status display at the FACP showed the detector had returned from 80% dirty to 0% dirty. The map uploaded in the SDU showed the device red and indicated in its properties that the person...
- Fri Apr 22, 2011 3:11 pm
- Forum: EST3
- Topic: SIGA-SD Maintenance Alert
- Replies: 8
- Views: 10834
Re: SIGA-SD Maintenance Alert
Thanks JimM.
After thoroughly cleaning the detector, the next day a map fault occurred. Diagnostics shows that the device personality had changed. Is this normal that you would need to reinitialize the loop and rectify after cleaning?
After thoroughly cleaning the detector, the next day a map fault occurred. Diagnostics shows that the device personality had changed. Is this normal that you would need to reinitialize the loop and rectify after cleaning?
- Wed Apr 20, 2011 8:55 am
- Forum: EST3
- Topic: SIGA-SD Maintenance Alert
- Replies: 8
- Views: 10834
SIGA-SD Maintenance Alert
Does anyone know the procedures used to clean a SIGA-SD duct detector? Does anyone know where to find the documentation. I have not been able to find it on UTC-EST website?
- Mon Apr 11, 2011 11:17 am
- Forum: EST3
- Topic: SDU & key used on different systems
- Replies: 1
- Views: 3523
SDU & key used on different systems
Is it possible to use an Edwards EST SDU and key on a Honeywell XLS1000 version of the EST3 and vise versa? I have a client very upset with Honeywell and wants to have our company perform any maintenance and upgrades, since we are already maintaining the access control and CCTV systems.